So I understand that this is not ideal before people jump in, but I am stuck with a 2.5mm feed to the garage.

2.5mm feeding garage 27m
1.5mm in garage for lights 30m
4mm in garage feeding sockets 28m

16A mcb in house CCU feeing garage
16A mcb in garage feeding sockets
3A mcb in garage feeding lights

Volt drop to garage = 3.38%
Total volt drop for lights = 3.93%
Total volt drop for sockets = 5.52%

This seem acceptable?
[ElectriciansForums.net] Is this acceptable??
 
Last edited by a moderator:
I've just run the maths on a few scenario's (my wife and daughters are shopping and I'm sitting in the car waiting for them!)

Sticking a 13A FCU inline for all sockets still leaves it just over 5% so doesn't help.
Going up to 6mm for the sockets circuit leaves it at 4.8%
Changing to a B10 breaker in the garage leaves it at 4.7%, but obviously could affect intended usage.
If it's left alone but 8m of cable can be lost and sockets moved accordingly then it becomes 4.9%.
 
I've put the numbers into my VD spreadsheet. I'm getting 1.3V drop for lights, 4.9V for sockets, and 7.6V for distribution. Assuming method C, those can be corrected to 1.1V, 4.4V, and 6.9V respectively, allowing for them never reaching the full 70 deg operating temp.

Just about meets VD for sockets, but not for lighting. I would still install it though, real world it aint going to be a problem.
 
When would you calculate VD?
The usual answer is if what you have is not one of the "standard circuits" in the on-site guide.

As above, mostly you get an idea from that book of typical length/cable/load combinations and it is only when you get outside of that, like here with a mix of cables, would you look closely.

The regs have 3% for lighting still, though really that is a hang-over from the days of filament lamps that are very sensitive to voltage. With LED lights I personally would not care about applying 5% to both categories, even though it is still not the official thing.
 
Any reason why he couldn't omit the FCU, and have everything off the 16A MCB?
Probably none, as the MCB provides fault protection and the loads are unlikely to be capable of overloading the cable. But I still like to have protection for lights that is below the rating of the cable and/or switches, even though it is probably unnecessary.

I guess it stems from seeing those now-long-banned adaptors in the 70s that would allow you to plug in a socket to a bayonet lamp fitting!
 
So the way that I’ve look at is as such. I cannot change the 2.5mm feed to the garage, it’s set, buried. I was going to leave a 16A feeding the garage from the house so that it does not draw more than this. The lights are obviously set at drawing a max 1.47A, the sockets could technically draw 16A, but I doubt ever will. Thinking like using a vacuum for a car, trickle charger for battery and maybe the occasional grinder/drill.
I’ve calculated VD using 70C tables. 3.93% for lights. 5.52% for power, but only using a 4mm. A 2.5 for power would make total VD 6.85% which is obviously too high. But it seems that people this both power and lights are still too high, but why? It doesn’t exceed 3% and 5% respectively, just decimal places, is this not acceptable?
 
Realistically, what load(s) are going to be used?

If it is a ghetto blaster and occasionally a 2kW heater then check the VD for that 9A load!

But do check the end of circuit Zs is good enough for the 16B MCB, that is a bit more important for safety.
I can see in winter something warming up without a Zs reading how will you know the 16 amp mcb will trip. I do hope you have the means to test.
 

Reply to Is this acceptable?? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
456
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
794

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top