Did some work for a friend and want to know if i did it right. As in regs compliant. I came off an existing lighting circuit to a sw fused spur. I used a 3A fuse to stop nuisance tripping. All the bends are done by hand and there was previously no conduit so i altered previous work. I sealed the all holes with silicone and made sure the connections were bomb tight. Im only newly qualified and did this off my own back. Any advice/ideas [ElectriciansForums.net] is this acceptable?[ElectriciansForums.net] is this acceptable?[ElectriciansForums.net] is this acceptable?[ElectriciansForums.net] is this acceptable?[ElectriciansForums.net] is this acceptable?[ElectriciansForums.net] is this acceptable? would be nice.
 
Hmm. The outside looks ok except the T+E which you are going to sort. As for the inside....
Pic 1 conduit looks horrible - Why not double set it so it looks level and tidy ? Looks like you used 1 saddle for that run too. You could have even kicked the conduit out near the top of the wall and run it in a straight line on the ceiling with a final right angle down to the box.
Pic 3 The spacing of the saddles looks wrong/horrible to close to the switches and bends. (But you are only following the other conduit drops which already have badly spaced saddles so you were kind of restricted.)
You form your own bends then ruin it by using an inspection 90....just don't look right.
Lack of saddles and badly spaced...Sorry bud if this comes over negative but if you are just starting out I am more of the camp that likes to point out the faults rather than hope you get better over time. At least you have the balls to post up and ask so kudos for that.

**Edit to add - that run of conduuit along the top did not even need a stop end....you could have went straight through the wall at top level and come into the back of a through box on the outside and went on from there.
 
Hmm. The outside looks ok except the T+E which you are going to sort. As for the inside....
Pic 1 conduit looks horrible - Why not double set it so it looks level and tidy ? Looks like you used 1 saddle for that run too. You could have even kicked the conduit out near the top of the wall and run it in a straight line on the ceiling with a final right angle down to the box.
Pic 3 The spacing of the saddles looks wrong/horrible to close to the switches and bends. (But you are only following the other conduit drops which already have badly spaced saddles so you were kind of restricted.)
You form your own bends then ruin it by using an inspection 90....just don't look right.
Lack of saddles and badly spaced...Sorry bud if this comes over negative but if you are just starting out I am more of the camp that likes to point out the faults rather than hope you get better over time. At least you have the balls to post up and ask so kudos for that.

**Edit to add - that run of conduuit along the top did not even need a stop end....you could have went straight through the wall at top level and come into the back of a through box on the outside and went on from there.

Are you for real? Clerk of works or what?:bobby:
 
I take the comments on board but I have just realised God status still needs to be achieved. [emoji1] I'm only 21 so I suppose I've got a while to perfect stuff.
Mate don't take my criticism to heart. I was more moved to comment when I saw you were just starting out......It's more to encourage you and get your head thinking hmm yep maybe I could have done this/that. Or even that Diddy is a grumpy fussy idiot....as long as you think lol.
My standard saddle placement is 12"/300mm away from each box/bend and saddles spaced out equally between as required. That makes for a tidy job that looks all symmetrical ect when you stand back and look at it. Like I say I know I am a fussy git....just trying to throw a few pointers out there to a newly qualified fellow spark. Be neat and tidy mate it will be what separates you from the chancres in our industry.
 
With the first pic, I would have liked to see an double set on that, BUT on the whole not bad at all, don't see an problem with using black pvc conduit externally (heavy gage), t&e outside not a good idea. but well done.
 
Did some work for a friend and want to know if i did it right. As in regs compliant. I came off an existing lighting circuit to a sw fused spur. I used a 3A fuse to stop nuisance tripping. All the bends are done by hand and there was previously no conduit so i altered previous work. I sealed the all holes with silicone and made sure the connections were bomb tight. Im only newly qualified and did this off my own bat. Any advice/ideasView attachment 26951View attachment 26952View attachment 26953View attachment 26954View attachment 26955View attachment 26956 would be nice.
​I changed that for you.
 

Reply to is this acceptable? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
350
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...
2
Replies
24
Views
3K
Hello Brianmoooore, Thanks for yor reply - Sorry that I did not see your message until today - the Forum replies notification emails about your...
Replies
7
Views
668

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top