I have broken into a ring, to feed an RCD spur to then go on to feed other items, but cant say as I would do it quite this way.

I am sure you have logical explanation in your head somewhere...
 
There is a bit in app15 (RFC part) that suggests appliance greater than or equal to 2kW should be fitted on their own dedicated radial circuit.
 
Basically he wants to run a rfc in kitchen for his appliances but use fcu's supplying double sockets. Instead of pulling appliances out to get to sockets he wants to fit fcu above worktop then run cable in wall to double sockets. If that makes more sense

There must be literally thousands of kitchens wired up exactly that way to provide isolation to under-counter appliances without having to touch the appliance. The other method is to fit appliance sockets in adjacent kitchen cabinet & drill out of sight hole to allow plug to pass through.
Either method is acceptable
 

Reply to is this allowable in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
524
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
982
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
915

Similar threads

Haha yes, it is. Must be a northern expression. Have a Google 😂
Replies
3
Views
410
  • Question
Thanks for the advice.
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top