S

Sparky83

Hi all,

I have just had a phone call from a mate of mine who's dad has had a sparky around to quote for a DB change, he was told that he would need the supplementry bonding back to this DB up graded due to the shower being fed in 10mm T&E?? Shower is a 9.5Kw shower.

It is apparently 4mm and goes back to the DB at present, is this something that would need upgrading?? I thought supplementry was something that aint that important anymore in the age of RCD's

Any help??

Cheers

Shawn
 
as long as the resistance between the pipes complies with bs7671 and an rcd is fitted to all circuits in the bathroom then supplementary bonding can be disconnected.
 
There is no need to take the supplementary bonding back to the consumer unit
Doing so is not correct, never mind the size of that supplementary bond
The faraday cage desire could be compromised by expanding the equipotential zone outside of the location

Does the zone require supplementary bonding,check out 701.415.2

If there is a need for supplementary bonding check out page 37 of the on site guide for the size required for the supplementary bond, by comparison with the protective conductor size
 
There maybe a mix up here with correct terms used.

Maybe the spark quoting for the mains change is on about the Bonding, (gas, water) Which he may have said needs upgrading to 10mm.
 

Reply to Is this correct?? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
523
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
982
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
915

Similar threads

As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
503
Heh I know the brochures for courses with stock images of women using tools in random scenarios but when you're there it never happens, it's all...
    • Like
Replies
2
Views
437

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top