Hello there a quick question if anyone would like to cast their view on it.
Ive been asked to do some electrical work in a laboratory i.e add some sockets to the existing bank of 10 twin sockets which are fixed to trunking.

On checking the existing sockets they are all on a 4mm radial. The incoming supply comes into the back of the trunking which is a 2.5mm ring circuit which runs about 15m down the corridor to the db. The ring circuit has no sockets connected to it, just runs to the trunking and back again. The connections for the radial to the ring is a chocolate block.
So if anyone can throw their opinion on this it would be much appreciated
 
is the block accessible? does it show signs of deterioration? not ideal situation. why did they not just make the whole circuit a RFC?
 
Well thats just the helpful answer i expected. Personally i don't think it is. But these labs are all the same, in UCl buildings in london and installed by large electrical firms. So how come they can get away it?
 
A bit like a big 4mm spur off a RFC...I think that if the connection to the RFC is sound and accessable as Telectrix has asked, then although unorthodox (spelling) it maybe ok.....
 
Well thats just the helpful answer i expected. Personally i don't think it is. But these labs are all the same, in UCl buildings in london and installed by large electrical firms. So how come they can get away it?

Don't be sarky, I asked you a question in the same way you asked a question.

If you can answer mine, then you will have your own answer.
 
there is no regulation that will say is not legal. current carrying capacity of 4mm in trunking is 32amps. if the lot is connected to 32a breaker then it may be bit unconventional but nothing wrong with it. test as a radial at furthest point.
 
Nothing much wrong with the unconventional wiring, but it's normal for ''laboratory sockets'' in schools to be a little more protected than just by RCD devices. But then again standards have fallen and continue to fall, so i'm not that surprised to be honest!!
 
My guess is that you might find that back in history the room had a few sockets on a ring, then got modified to how it is now. As others have said, if the CPD is suitable for the lesser of the cabling conventions and disconnection times/Zs for it are being met then it complies with the requirements of BS7671. It might be more compliant, however, if you swapped those choc-bloc screw terminals for something MF based instead.

Oh.....and if I were in your shoes..... I'd be wondering why it is that you've been asked to do this work instead of 'the big firms' that have been in there previously - has someone got upset with somebody?
 
Hello, no, the big outfits are still in there, their not interested in doing the small little labs anymore, they more or less please themselves with that.
The labs have generally 2 different supplies. Non essential which is on a ring 2.5mm and rcd protected, the essential supply which is what I'm looking at it, is a separate feed as i first mentioned.
Its just why run a ring in 2.5mm then branch off with a 4mm radial?
But thanks anyway
 
If it were a 'proper' ring serving multiple sockets, with a 4mm branch coming off it serving multiple sockets, then the concern would be potentially overloading one point of the ring. What you've got there is better described as conductors in parallel for the first part. Probably!
 
If it were a 'proper' ring serving multiple sockets, with a 4mm branch coming off it serving multiple sockets, then the concern would be potentially overloading one point of the ring. What you've got there is better described as conductors in parallel for the first part. Probably!

It is indeed, provided that those two parallel conductors comply with all the requirements of a parallel circuit.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Is this legal
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
21
Unsolved
--

Advert

Thread statistics

Created
Comftybold,
Last reply from
Engineer54,
Replies
21
Views
2,383

Advert

Back
Top