Guys in a solar PV plant room I have a single phase LV board for power and lighting. This is fed via 2 phases off a solar inverter through a 415 > 230v Isolating transformer.
The earth conductor in the secondary side of the transformer is not connected. Theres a 16mm cpc going from the LV board to an earth bar which is the main earth bar for the plant room.
I cannot get the RCDs to trip on this LV board (assuming due to the isolated supply)? Even on the inverters I cannot get a Ze reading at all as my meters are coming up with no earth connection. I'm again assuming this is a completely isolated supply but how do I get the RCDs to operate? do i connect the disconnected earth up to the neutral in the transformer???
Really racking my head this one, any help would be great.
The earth conductor in the secondary side of the transformer is not connected. Theres a 16mm cpc going from the LV board to an earth bar which is the main earth bar for the plant room.
I cannot get the RCDs to trip on this LV board (assuming due to the isolated supply)? Even on the inverters I cannot get a Ze reading at all as my meters are coming up with no earth connection. I'm again assuming this is a completely isolated supply but how do I get the RCDs to operate? do i connect the disconnected earth up to the neutral in the transformer???
Really racking my head this one, any help would be great.