Hello fellow sparks.
Just a query about a job i've been asked to do recently. I've been planning it, regarding the cable sizing and method(s) of protection required. Client is thinking of having a Swimming Pool installed and the Heater is 20KW !! Roughly Equating to 80 Amps..! The Service Fuse for the House is 100 AMP,
I realise because it is a BS88 Cartridge Fuse it will not blow at 100, So due to this , and diversity factor 180 Total should be fine?!!? (Or possible get onto electricity board for an extra phase installed??!
If i did tap of Existing supply, using Henley Connecter, with 25mm cable into 80Amp Switch Fused Isolator, then 25mm Armoured cable buried across the garden into another CU close to Swimming pool.. The regs state you must provide R.C.D protection AND over-current protection. So was thinking about using 80 AMP R.C.D with 80 AMP Cartridge fuse. As i cannot find 80amp M.C.B. or 80 amp R.C.B.O anywhere..??! Ive used the correction factor with the BS88 Fuse, and Cable size still sufficient. I realise there must also be an Isolator Switch aswell,, Heavy Duty Rotary ON/OFF switch maybe.?
Does Anyone Have any ideas or come across similar situations in the past?? I'm trying to do it to the regs and apply correction factors where necerssary.. Major dilemma is whether or not to have an extra phase installed..?!
Just a query about a job i've been asked to do recently. I've been planning it, regarding the cable sizing and method(s) of protection required. Client is thinking of having a Swimming Pool installed and the Heater is 20KW !! Roughly Equating to 80 Amps..! The Service Fuse for the House is 100 AMP,
I realise because it is a BS88 Cartridge Fuse it will not blow at 100, So due to this , and diversity factor 180 Total should be fine?!!? (Or possible get onto electricity board for an extra phase installed??!
If i did tap of Existing supply, using Henley Connecter, with 25mm cable into 80Amp Switch Fused Isolator, then 25mm Armoured cable buried across the garden into another CU close to Swimming pool.. The regs state you must provide R.C.D protection AND over-current protection. So was thinking about using 80 AMP R.C.D with 80 AMP Cartridge fuse. As i cannot find 80amp M.C.B. or 80 amp R.C.B.O anywhere..??! Ive used the correction factor with the BS88 Fuse, and Cable size still sufficient. I realise there must also be an Isolator Switch aswell,, Heavy Duty Rotary ON/OFF switch maybe.?
Does Anyone Have any ideas or come across similar situations in the past?? I'm trying to do it to the regs and apply correction factors where necerssary.. Major dilemma is whether or not to have an extra phase installed..?!