Ay up lads

I'm about to install 10mm2 5 core swa for 63 amp chiller protected by 63a MCCB, should I provide rotary isolator for it? Chiller must be working 24h/7

Its my first industrial install and probably my pay rise depend on it. I know there is the reg saying "means of isolation shall be provided" but the chiller needs to be permamently on and powerd up through a 5pin plug. Can you help guys?
 
Ay up lads

I'm about to install 10mm2 5 core swa for 63 amp chiller protected by 63a MCCB, should I provide rotary isolator for it? Chiller must be working 24h/7

Its my first industrial install and probably my pay rise depend on it. I know there is the reg saying "means of isolation shall be provided" but the chiller needs to be permamently on and powerd up through a 5pin plug. Can you help guys?
Fit a switched 5 pin socket outlet, capable of being locked in the OFF POSITION. With interlock to st an inadvertent removal of the plug on load.
 
Fit a switched 5 pin socket outlet, capable of being locked in the OFF POSITION. With interlock to st an inadvertent removal of the plug on load.

Cheaper to just fit a rotary isolator. Why install a socket? If this machine is to run 24H it's hardly something portable. It'll be fixed in place with pipe work and heat ex changers.

Edit: Sorry, I miss read the OP. Didn't see it came with a plug. Even still, I would take it off and wire into a normal rotary isolator installed next to the machine.
 
Cheaper to just fit a rotary isolator. Why install a socket? If this machine is to run 24H it's hardly something portable. It'll be fixed in place with pipe work and heat ex changers.

Edit: Sorry, I miss read the OP. Didn't see it came with a plug. Even still, I would take it off and wire into a normal rotary isolator installed next to the machine.
I would keep the plug, reason although hopefully you would have carried out the safe isolation correctly, the sight of a plug dangling by the machine would give you greater confidence that the machine was in fact isolated, in my opinion anyway.
 

Reply to Isolator for 63A chiller? in the Talk Electrician area at ElectriciansForums.net

Similar Threads

  • Question
Required under certain circumstances.
Replies
10
Views
3K
We’re in Manchester, so a bit of a trek, but thanks for the offer 😃
Replies
11
Views
2K
Yeah that's what I did in the end. I got data sheet from the manufacturer and calculated the max Zs for each of them.
Replies
8
Views
2K
  • Question
Make sure any plan fully considers the EVCP as this as it can affect several factors of this design. You certainly don't want a 13amp EVCP. (In...
Replies
13
Views
5K
There's no reason there to spend the extra. The advantages of a combined cable are neatness and speed of installation.
Replies
10
Views
5K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks