marshr02

Hi there. If my supplier does not install DP isolators (CU side of Meter) am I right in thinking there is nothing stopping me from installing one - or will they throw a wobbly when they come to refit the fuse (no meter fairies). Also would you slap it on 'their' board on the basis that the meter really should have an inbuilt isolator - so that is where it should be rather than on the CU board nearby (which has no space). Cheers for any opinions....
 
just install it between meter and CU. anyone asks " it's been there since before i moved in"
 
Been there 20 years and the CU is shiny new, choc full of RCBOs. The REC isolator is one of the reasonably new Wylex jobbies. So...not sure the old it's been there since 1950's line will work in the case. Also my other question - would you slap it on the meter board?
 
the consumers installation technically starts at the load side of the meter terminals.
therefore you are perfectly within your rights to fit an isolator or any other suitably rated device prior to the CU
;-)
 
would you slap it on the meter board?


i'd put it in the most convenient place, depending on how the tails run. irrespective of whether it's on the boarfd or not.


 
Thanks for the replies. Why? Obviously we should all be able to pull the main fuse without prosecution AND obviously the new smart meters (that will report pulled fuses) will have an inbuilt SP isolator (!) BUT seeing as none of the above actually apply then unfortunately it seems the only way to go is to fit an isolator OR live working. Does anyone have any opinion about increased fire risk re more terminals to possible be loose?
 
Murdoch - I'm thinking of leaving as is i.e no isolator (other than the fact that I'm replacing the CU at the moment) BUT I though everyone was getting p'eed off with working live or waiting around half the day for the DNO to visit to de-energise. (Remember after Smart meters the fuse fairies will not exist)...
 
ask it a question similar to those on millionaire for the 20grand. if it gets it right, it's a smart meter.
 

Reply to Isolator for CU in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
93
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
889
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

I would hazard a guess your electrician may be able to contact your DNO and have the switch swapped to a MFS very quickly..
Replies
13
Views
790
  • Question
If it's buried ducting, have you thought about digging up a section of the buried cable close by, cutting it and pulling in a few extra meters...
Replies
6
Views
905

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top