Hi ! Situation is this , 10mm t&e approx run 10 M , 10-10.5kw Shower, 60898 40 amp , I recently( February) replaced isolator due to overheating( neutral load side) . Installed a mid price range (45a)new one , made sure off good tight connections , but now have same problem overheating load neutral side again , any advice, do I need to refit better quality isolator or could there be a fault with shower unit? Had this numerous times and just replaced isolator as loose connections, arching are common problems! Cheers
 
Hi ! Situation is this , 10mm t&e approx run 10 M , 10-10.5kw Shower, 60898 40 amp , I recently( February) replaced isolator due to overheating( neutral load side) . Installed a mid price range (45a)new one , made sure off good tight connections , but now have same problem overheating load neutral side again , any advice, do I need to refit better quality isolator or could there be a fault with shower unit? Had this numerous times and just replaced isolator as loose connections, arching are common problems! Cheers
are you sure?...

did you `rattle` the cable about in the terminal and check again?...chances are after the strands have spread & bedded down the terminal screw will go at least another 1 1/2 turns....

you will know when its there....
 
These 10.5KW and above showers are just a joke anyway. No-one really needs a shower rating of that size. Can't really see any point in the things being over 8.5 to 9KW max!! The shower unit i am using here, is 4.7KW and it's delivers more than enough hot water than i can bare!!

As for the 45A isolator switch, use Crabtree, MK, or other good quality units on high current accessories.
 
what folk completely and utterly fail to realise is that increasing the wattage / power of an electric shower is only of benefit if the water pressure is good enough to make use of the higher rating.
otherwise its just a boiling hot dribble lol.
 
what folk completely and utterly fail to realise is that increasing the wattage / power of an electric shower is only of benefit if the water pressure is good enough to make use of the higher rating.
otherwise its just a boiling hot dribble lol.

But a lower wattage shower will not give the same water temperature as a higher wattage shower for the same water flow !!
This is where higher wattage showers are better as you can have higher flow and hotter water. I have never come across a shower that gives sufficiently hot water at max water flow.
 
But a lower wattage shower will not give the same water temperature as a higher wattage shower for the same water flow !!
This is where higher wattage showers are better as you can have higher flow and hotter water. I have never come across a shower that gives sufficiently hot water at max water flow.

i have never seen any electric shower of any wattage thats anywhere near as good as a power or mixer shower which is due to having pumped water supplies.
to get the most out of any increased wattage you need a correspondingly good water pressure
 
i have never seen any electric shower of any wattage thats anywhere near as good as a power or mixer shower which is due to having pumped water supplies.
to get the most out of any increased wattage you need a correspondingly good water pressure

I take it you mean flow as opposed to pressure.

Like electricity, volts are no good without amps.

Not an epic fail (as you like to point out according to your signature) just confused I guess ; )
 
Last edited:

Reply to Isolator overheating in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
865

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top