Draft of DTI Guide third edition no longer mentions need for padlock.
[FONT=Helvetica, sans-serif]A.C. Switching Device[/FONT]
[FONT=Helvetica, sans-serif]Switching of the a.c. side of the installation shall comply with the requirements of BS7671,[/FONT]
[FONT=Helvetica, sans-serif]An a.c. switch or combination of switches must be provided for isolation and maintenance in the installation.[/FONT]
[FONT=Helvetica, sans-serif]A switch for mechanical maintenance shall be provided in close proximity to the Inverter and shall fulfil the following conditions: [/FONT]
[FONT=Helvetica, sans-serif]Switch all live and neutral conductors [/FONT]
[FONT=Helvetica, sans-serif]Be securable in the OFF position only[/FONT]
[FONT=Helvetica, sans-serif]Clearly show the ON and OFF positions and be labelled as 'PV system - main a.c. isolator'[/FONT]
[FONT=Helvetica, sans-serif]An accessible means of isolation shall be provided to isolate the a.c. circuit . MCBs, RCDs and main switches installed in accordance with BS7671 and in an accessible location can be used to fulfil the requirements for an accessible means of isolation. [/FONT]
[FONT=Helvetica, sans-serif]Note: At the point of installation of any a.c. switch-‐disconnector, the public supply should be considered the source and the PV installation the load.[/FONT]