Im working on a brand new ww pumping station and have an issue with the above.
DESCRIPTION (I know, should have photos)
New mcc panel with 80a main switch/change over (genny inlet).
HMI, PLC, Profibus to Hydroranger, VSDs, etc.
2 pumps @22kw fed from mcc section c and d, 50a fused.
Mcc is in a 2m high kiosk and to the right there are 2 vsds and the pump feeds exit in their own ducts immediately below them with a 10mm parallel cpc.
To the left side there is a magflow head and a Hydroranger 200.
Magflow cables and ultrasonic cable exit in their own duct towards the middle of the kiosk.
Separate ducts go through manholes and the pump supplies and ultrasonic cable enter the valve chamber where each has its own jb.
The banjos for pumps and ultrasonic armours are bonded back to the local traywork.
Final pump tails (Flyght) and u/sonic vendor cable come through from the well in separate ducts.
Hydroranger to u/sonic jb is wired in 0.75 3 core screened bs 5308 cable.
PROBLEM
Ultrasonic level is displayed acurately but when the VSDs kick in (reverse first then forward) the Hydroranger freezes its display and then starts to rise although the magflow confirms out flow. Then of course we have a potential dry running.
If we disconnect the cpc from the Hydroranger the problem goes away and the pumps obey the setpoints. The cpc comes from the common controls section with the L&N in plastic trunking/kopex.
The Hydroranger has relay number one set for dry run protection but in this scenario its useless.
Any experience?
Boydy
DESCRIPTION (I know, should have photos)
New mcc panel with 80a main switch/change over (genny inlet).
HMI, PLC, Profibus to Hydroranger, VSDs, etc.
2 pumps @22kw fed from mcc section c and d, 50a fused.
Mcc is in a 2m high kiosk and to the right there are 2 vsds and the pump feeds exit in their own ducts immediately below them with a 10mm parallel cpc.
To the left side there is a magflow head and a Hydroranger 200.
Magflow cables and ultrasonic cable exit in their own duct towards the middle of the kiosk.
Separate ducts go through manholes and the pump supplies and ultrasonic cable enter the valve chamber where each has its own jb.
The banjos for pumps and ultrasonic armours are bonded back to the local traywork.
Final pump tails (Flyght) and u/sonic vendor cable come through from the well in separate ducts.
Hydroranger to u/sonic jb is wired in 0.75 3 core screened bs 5308 cable.
PROBLEM
Ultrasonic level is displayed acurately but when the VSDs kick in (reverse first then forward) the Hydroranger freezes its display and then starts to rise although the magflow confirms out flow. Then of course we have a potential dry running.
If we disconnect the cpc from the Hydroranger the problem goes away and the pumps obey the setpoints. The cpc comes from the common controls section with the L&N in plastic trunking/kopex.
The Hydroranger has relay number one set for dry run protection but in this scenario its useless.
Any experience?
Boydy