G

guest119

Im working on a brand new ww pumping station and have an issue with the above.

DESCRIPTION (I know, should have photos)

New mcc panel with 80a main switch/change over (genny inlet).
HMI, PLC, Profibus to Hydroranger, VSDs, etc.
2 pumps @22kw fed from mcc section c and d, 50a fused.
Mcc is in a 2m high kiosk and to the right there are 2 vsds and the pump feeds exit in their own ducts immediately below them with a 10mm parallel cpc.
To the left side there is a magflow head and a Hydroranger 200.
Magflow cables and ultrasonic cable exit in their own duct towards the middle of the kiosk.
Separate ducts go through manholes and the pump supplies and ultrasonic cable enter the valve chamber where each has its own jb.
The banjos for pumps and ultrasonic armours are bonded back to the local traywork.
Final pump tails (Flyght) and u/sonic vendor cable come through from the well in separate ducts.
Hydroranger to u/sonic jb is wired in 0.75 3 core screened bs 5308 cable.

PROBLEM

Ultrasonic level is displayed acurately but when the VSDs kick in (reverse first then forward) the Hydroranger freezes its display and then starts to rise although the magflow confirms out flow. Then of course we have a potential dry running.
If we disconnect the cpc from the Hydroranger the problem goes away and the pumps obey the setpoints. The cpc comes from the common controls section with the L&N in plastic trunking/kopex.
The Hydroranger has relay number one set for dry run protection but in this scenario its useless.

Any experience?

Boydy
 
have you earthed the screening on your screened cable? seen problems before with an ungrounded screen acting as an aerial,some even have a drain wire inside with the cores.
 
The screen is connected to the ultrasonic screen core at the jb end and to the screen connection in the Hydroranger.
So at no point does it connect to the wire armour Phil.
The spare core also is connected at both ends with the screen.

Boydy
 
Screens need to be connected at BOTH ends and with a nice 360 degree circular connection. If there is excessive current in the screen then run another conductor in parallel.
 
What is the wiring from the head to the 3 core?

No doubt you had an manual, but.
Just a thought saw some contractors common the white with shield before accidently.

When connecting to a SITRANS LUT400, a SITRANS LUC500, a MultiRanger 100/200, or a HydroRanger 200, the white, black, and shield wires are all connected separately.DO NOT tie the white and shield wires together.





[ElectriciansForums.net] Issue with Hydroranger 200.
 
Last edited:
Its a Siemens xps 15 in this instance.
Shield to shield of the bs5308 swa and black/white (ultrasonic) to black/blue (swa).
Its a commissioning issue now as Im install.
I'll report back when I find out so as to help others.
When I left on Friday the commission guy was messing about with earthing at the vsd gland plates and seemed confident he knew the issue.

Boydy
 
Right then, where to begin?

I havent been on site but I spoke to the commissioning engineer and he says its sorted.

We had a 4 core swa running to the pumps jb and only used 3 cores.
We also had a parallel earth wire.
At the pumps jb the parallel earth is the pumps cpc and the swa is just banjoed to the containment.
At the VSD we took the parallel earth to a stud on the gland plate (external) and off the same stud (internally) to the VSD pump earth connection, all because there was no space for a stuffer for the parallel earth.

Anyway, he used the spare core straight to the VSD output earth connection and connected it in the pump jb instead of the parallel earth.
Now no more Hydroranger problems.
Way above my head but something about square waveform dc switching by the VSD puting noise on the earthing.

So one for me to remember, the pump earth/cpc needs to go right into the VSD output connection and not to the glandplate. VSD glandplate is for swa banjo/containment only which apparently is somewhere in the Simatics instructions.

Phew!

Boydy
 

Reply to Issue with Hydroranger 200. in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
939
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
When you did the further testing and got the 0.06 reading were the CPC's back in the consumer unit? Really when testing you should leave the...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top