In a domestic, none of the 3 ring mains comply with the 0.05 difference between sockets, some readings varied drastically, anyway I'm sure they're not proper rings, rewiring them is not an option. Could I just fuse it down to a 20amp breaker and leave both tails in the MCB or would I have to leave one out and put it in connector block?

I think ring mains shouldn't be allowed in places that don't get regular periodic inspections, (such as domestic) but anyway thoughts?
 
Is you final ring cable 2.5/1.5 or 2.5/1.00 ?

When testing are you sure you have the correct legs cross connected in the figure of eight.
When testing at socket outlets without removing the socket you can get high readings.
If you are going to reduce the mcb down to a 20 A you will have to split the ring at the CU and somewhere on the ring to make two radial circuits.
If you leave both legs in the same mcb you will have one mcb covering 2 radial circuits only allowing a max of 4600w.
So you will have to see what the demand for the circuits are going to be.
I would trace the fault and leave the CCT as final ring circuit.
 
the sockets are old, i really should have taken them off and checked it from the inside, I was going through it a bit quickly since I'm basically just doing it as a favour for a mate as I'm out of work and got nothing better to do. I going to go back anyway and I'll thoroughly inspect it next time and try and trace whats going on. The upstairs and the kitchen I can easily believe its just the sockets from what I was getting and the state of the sockets but I'll have a closer look. Just really wanted to know if it came down to it what would be the non rewire option. thanks tony, I doubt it'd get up to 4600w, but hey who knows.

Edit:
the ones with high readings i did open up and they weren't spurs atleast they shouldn't be having in and out, but when i look again maybe i'll find a strange end of line. probably should have tested them again from the inside while I had the ones that i had open, but this time i didn't. I think you might be correct about 2.5 / 1.0 cable thats unusual, when was that ever allowed? Now it has to be 2.5/1.5 or 1.5 / 1.0 if it has been fused down. I havn't managed to get around to fault finding yet. Just had a quick look really.
 
Last edited by a moderator:
IR test just did off the busbar got like 8 megaohms for the circuits on the board. After reading these posts and thinking about what i saw, It could just be a combination of faulty sockets (as i was testing off the sockets) and change in CPC sizes, as theres stranded AND solid core cable in the circuit same for the others and i think theres 2.5 / 1.5 and 2.5 / 1.0. even having it cross connected at the board, testing at different socket outlets a change in cpc size could affect the readings right?
 
well I did the cross connection to opposite legs (R1 to R2), tested Zs which varied aswell, stupidly didn't write down anything except the highest which was .50 oddly. Just baffled now thinking if its just because of cpc changing size how will I be able to prove its a proper ring without being able to trace the cable, or am I over thinking it now? Man I just want to go back and do a fresh install where I don't have to fault find unless some idiot has pinched a cable on a trunking buckle.
 
Ring Finals for the main house sockets/radials in 4mm for kitchens and 2.5mm garages/outhouses. Reduce the in between times for periodics on domestic. The idea with rings was to spread the load evenly (although this is sometimes abused) but the disadvantage is if there is a break in the cable it will still be energised both sides of the break

Why are you trying to label and restrict uses for final circuits here?? You design and install a final circuit as to the requirement of the installation, and for no other reason. There are up sides and down sides to both ring and radial final circuits.

This old chestnut about breaks in ring finals, is what many highlight, in reality they are about as common as a radial losing it's CPC along the line, ...Rare!!!
 

Reply to its not a proper ring! in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
298
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top