I have a garden shed supplied with power from the main CU in the garage. It runs down the garden in SWA, everything is in accordance to regs except possibly at a junction between SWA and T&E. The circuit starts off in T&E and on the outside of the garage wall, in a IP rated enclosure, it goes to the SWA. Should there be a fuse here? Or is that just the case just when you join a smaller cable on to a bigger one? They are both the same csa. cheers.
 
I have a garden shed supplied with power from the main CU in the garage. It runs down the garden in SWA, everything is in accordance to regs except possibly at a junction between SWA and T&E. The circuit starts off in T&E and on the outside of the garage wall, in a IP rated enclosure, it goes to the SWA. Should there be a fuse here? Or is that just the case just when you join a smaller cable on to a bigger one? They are both the same csa. cheers.[/QUOTE

No as long as your join is in the correct enclosure and accessible there is no need for a fuse.

NB. Your shed should be on a TT system as it is outside the main equipotential zone.
 
Not strictly correct.

You can export the earth, however, if there are services in the outbuilding, then these must be bonded back to the MET in the house normally via 10mm G/Y.

This isnt very practical and so most people tend to TT the outbuilding and bond to the stake.

:)
 
Not strictly correct.

You can export the earth, however, if there are services in the outbuilding, then these must be bonded back to the MET in the house normally via 10mm G/Y.

This isnt very practical and so most people tend to TT the outbuilding and bond to the stake.

:)


Didn't know that one but yes it makes sense though as stated not very practical.
 
Thanks for the answers - there is no gas or water there and the little CU down there is connected to an earth spike. However, the earth of the swa (it is a 3 core, the armouring has not been used) is connected back to the main CU as well - is that ok?
 
Thanks for the answers - there is no gas or water there and the little CU down there is connected to an earth spike. However, the earth of the swa (it is a 3 core, the armouring has not been used) is connected back to the main CU as well - is that ok?

The armouring of the SWA should be earthed to protect the cable from damage.

The earth from the main CU should not be connected to the earth from the shed CU. This should only be connected to your earth electrode making it TT.
 
There is no requirement for outbuildings to be separated from a TNCS earth except where TNCS restrictions apply...ie construction sites,swimming pools etc. A TNCS system with RCD protection can be used for a garden outbuilding
 

Reply to joining cables. in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
813
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

Sounds more positive.
Replies
8
Views
613
  • Question
This charger doesn't support rear entry from the looks, only bottom entry, hence that. Unless they make a white sheathed SWA, I would still need...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top