B

brman

I was taught that the main bonding should be continuous, including from the water to gas for example. However I am struggling to find a reg that states that. Can anyone point me in the right direction?

I ask because I have an installation where the gas isn't bonded, despite being only 2 feet from the water (which is bonded). So the bonding needs extending to the water.
It also has a junction in the back of the airing cupboard where it looks like some supplementary bonding has been joined in.

I am not too keen on replacing the 10m of 10mm back to the CU for the sake of it but will if it is deemed necessary. Is there actually a reg that says I need to?

I do need to get this one right as it is going to be assessed by elecsa in a couple of weeks time.....
 
Thanks Murdoch.

I've just been doing some more searching and found a big long thread here on the subject. It does appear it isn't a reg (or at least only a very tenuous interpretation of one!) but is in GN8.

As this is for my assessment I might just spend the extra on it ;)
 
IMHO you can "repair" the cable at the junction by through crimping and heatshrinking over the join, the supplementary bonding is only required to link earth terminals and extraneous conductive parts locally so doesn't need to be taken back to the CU. I would then apply the same logic and "repair" the cable in order to extend it to include enough cable to bond the gas and water together.
 
beaten to it by sjm. if you through crimp the existing 10mm bonding cable with a "permanent" joint, it's then continuous. take it off the water, crimp on a piece long enough to reach the gas and without breaking carry on to te water.
 
Thanks guys, strangely enough that is exactly what I did today. Except I soldered rather than crimped.

I managed to pull through enough to get the bonding to reach the gas so that didn't need extending so I ended up just replacing a short run to the eves (it was undersize) and removing the supplimentary bonding that joined to it as it did not appear to connect to anything. Not really a surprise as all the plumbing in the bathroom is plastic so I suspect the bonding was just left connected one end when that was done.

Anyway, job done :)
 
nothing wrong with solder. without it there would be no computers, no internet, no television. ahhh.... sod the guy who invented solder
 
I tell you what though, as much as I like soldering things, it would have been a lot quicker to crimp it and I wouldn't have singed my eyebrows when I set some cobwebs alight :lol:
 

Reply to Junctions in main bonding? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
607
loz2754
L
  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top