Can anybody help me please?

I'm servicing a Juno 1-3 fire alarm and the display reads 'Power fault. battery disconnected, check fuse' & 'alarm fault on sounder circuit 3' i replaced the batteries, like for like, but the fuse hold was loose, fuse tested ok. I then swapped the sounder circuits ie connected circuit 2 to 3 & 3 to 2, and the result was still 'fault on sounder circuit 3' ie the wiring was ok, but again the fuse was loose in the holder. I replaced the circuit board with a new one, re connected everything but the 'battery fault' still exists and a new fault of 'Fault, beam detector faulty' has appeared, even though this was tested and worked ok previously. The sounder 3 circuit fault has cleared.

Can anyone give me some advise or tips?

Cheers
 
check that you are getting a charge voltage to the batteries..approx 26-28 volts d.c. if nothing find charger fuse and check it.make sure battery terminals are clear from any corrosion.why you have a new fault appear is mysterious.connect you lappy to it and interrogate the panel to find analogue value of that specific detector.cant advise much more than this.
 
The old Trident panel remarketed as Juno...As above check psu outputs, fuses, etc.
Find out where the beam detector is powered from, my bet is the Juno aux output hence the new fault.
Would deffo do as Nrvolts has said to download the panel...they used to have a great habbit of crashing and without the data to reload, you can find yourself reprograming the lot from scratch. Can only think the psu board is faulty.
 

Reply to Juno 1-3 Fire Alarm in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
917
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K
I have an AC system that is not working. All fuses and relays tested successfully. Blower comes on, but blows hot. System is completely empty...
Replies
0
Views
468

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top