D
Darkwood
Just installing some 50mm earth bonding to Gas and Water supplies in a factory, now the factory only has small service pipes for both as they are only really needed for office and works toilets so we have a incoming similar to domestic, im understanding the need re' incomming N size and PME systems and earthing must be large enough to cope with circulating currents that can form between other installations etc....my head scratcher is that to cope with these possible currents my earth to the gas has to be 50mm (N =185mm)but the gas pipe itself has nothing like the copper content or current carrying capacity of the earth im attaching to it, couldn't this cause rise to in extreme circumstances an overheating of the main gas line?