Bugger I think the 1.2 factor is right for the voltage drop - got that completely wrong then!
Be interested to see the paper again

Not sure about 1.2 factor for volt drop, are you sure your not thinking of the X 0.8 tempreture correction factor for tabulated Zs to measured Zs .
 
Hi did the volt drop question give you a resistance at 20C or a table with the m/ohm/m values at 20c if so then needed correcting by 1.2 for the increase in temp due to load current ie say a 1.83 m/ohm/m =10mm conductor with another added in parallel ie line and neutral at 20c will need increasing by 1.2 as its a conductor bunched or a core in a multicore cable for thermoplastic (pvc) 70C max operating temp
table A.3 in GN3

m/ohm/m x 2 x MF x Ib X L/1000 = Vd
1.83 x 2 x 1.2 x Ib x L/1000
which will give same value as the mv/A/M tabulated value from the regs when using
mv/A/M x Ib X L/1000
or
R1+RN x 2 x Mf x Ib x L/1000

be good if someone could remember the question or somehow found the paper in there bag lol


this sounds like a question i had for the 2391 june 2010 and the only thing i forgot to include was the MF of 1.2 which i realised later when discussing it with forum members
good luck to you all
 
Hi did the volt drop question give you a resistance at 20C or a table with the m/ohm/m values at 20c if so then needed correcting by 1.2 for the increase in temp due to load current ie say a 1.83 m/ohm/m =10mm conductor with another added in parallel ie line and neutral at 20c will need increasing by 1.2 as its a conductor bunched or a core in a multicore cable for thermoplastic (pvc) 70C max operating temp
table A.3 in GN3

m/ohm/m x 2 x MF x Ib X L/1000 = Vd
1.83 x 2 x 1.2 x Ib x L/1000
which will give same value as the mv/A/M tabulated value from the regs when using
mv/A/M x Ib X L/1000
or
R1+RN x 2 x Mf x Ib x L/1000

be good if someone could remember the question or somehow found the paper in there bag lol


this sounds like a question i had for the 2391 june 2010 and the only thing i forgot to include was the MF of 1.2 which i realised later when discussing it with forum members
good luck to you all

Hi Brucelee, From memory the question said something like: the combined resistance of the line and neutral is ?? ohms can you calculate the volt drop on these conductors,
as Jstephens said he got 11.4v I think I did too
But I am sure that I forgot to put a 1.2 correction factor into the equation,
Cheers Chris.
 
you definetly have to use the x 1.2 to allow for max operating temp of 70 degrees, i did the same exam
just passed my practical today!!!
 
Last edited:
I wonder how many marks you loose for not putting the correction factor into the equation or if you get no marks for the whole question :confused5:
 
Hi mate you should get something but how many marks not sure and as far as C&G you will never know now

would be good if you got your paper marked and sent back so you could brush up on areas that you hadnt done to well but all you get is its just pass or fail

good luck mate i felt the same after my exam wondering if i had done enough nothing you can do now except wait for the outcome

HOPE ITS GOOD NEWS for you
 

Reply to just took my 2391 test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

  • Question
There isn't anywhere to really revise on this it is down to knowledge and experience of seeing a scenario and seeing what is wrong if anything. If...
Replies
4
Views
2K
  • Question
My older card has it but my newer card doesn’t
    • Like
Replies
1
Views
501
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
Replies
21
Views
1K
It’s sad that you had to say no more money to them for them to pull their fingers out.
Replies
9
Views
774
so Ze 0.35Ohms and my Part of the Circuit just half of R1+R2 is 0.19353Ohms as its 1.5mm x 10m so well under but dont know of any switch gear...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks