Well I actually dug my osg out last night, dusted it off and cleaned the cobwebs away, and yes it's in there!Agree, it should disconnect sooner rather than later. But it is a struggle to find a circuit where SC loop impedance would the limiting factor, at least for the type of work I do. Voltage drop almost always gets there first. Very lightly loaded, very long lighting circuits perhaps.
The OSG paragraph is in my previous post #24, but doesn't link to a regulation, and I can't find anything in the regs that directly back it up.
That note and looking at the table suggests the loop impedance is the most common limiting factor without a rcd, and my experience would be the same, although the only real occasion in my experience is long remote lighting with small loads.
I don't know of a regulation which determines a required trip time, but obviously there's a subsection for fault protection which doesn't seperate a need between line-line, line-neutral, or live-cpc/earth, basically demanding protection for all types of fault current, whist live-cpc/earth faults do have a specific set of disconnection times