B
brman
I feel a little embarrassed asking a this as it is pretty fundamental and I thought I knew the answer but someone asked me this today and I couldn't justify it according to the regs. So.....
How come we can use 2.5mm2 to feed an unfused spur from a ring? (eg a double socket or even a FCU not actually on the ring)
2.5mm2 won't take 32A so isn't protected upstream by the 32A MCB. I thought it relied on downstream fusing but.........
Reg 434.2.1 says you can downstream protect a cable if there are not branches and it is less than 3m long BUT (ii) states that the cable must be "installed in a manner to reduce the risk of a fault to a minimum" and notes that, for example this could be "reinforcing the protection of the wiring" which I take to mean mechanical protection.
So, the way I read it, a standard 2.5mm2 cable to an unfused spur isn't allowed because it doesn't meet 434.2.1 part (ii). However it is of course standard practice and shown in Appendix 15, standard circuits.
What have I missed?
How come we can use 2.5mm2 to feed an unfused spur from a ring? (eg a double socket or even a FCU not actually on the ring)
2.5mm2 won't take 32A so isn't protected upstream by the 32A MCB. I thought it relied on downstream fusing but.........
Reg 434.2.1 says you can downstream protect a cable if there are not branches and it is less than 3m long BUT (ii) states that the cable must be "installed in a manner to reduce the risk of a fault to a minimum" and notes that, for example this could be "reinforcing the protection of the wiring" which I take to mean mechanical protection.
So, the way I read it, a standard 2.5mm2 cable to an unfused spur isn't allowed because it doesn't meet 434.2.1 part (ii). However it is of course standard practice and shown in Appendix 15, standard circuits.
What have I missed?