Location
Prestatyn
hi whilst testing ELI on lighting circuits, using kewtech kt63 on loop no trip function, test keeps tripping rcd once polarity and voltage is confirmed. I know the kt63 tests at 250v in this mode, but it shouldn’t trip the rcd, anyone else experienced this? Is it calibration time? Is it me? Is it the rcd? Anyone’s thoughts, and I know the calculation is Zs =(Ze + r1r2), a bit frustrated the damn things keep tripping, upstairs and downstairs, separate circuits, separate rcds, both trip.
 
My 63 has been a great buy, this one is strange. No doesn’t have ramp the 65 is a step up from the 63.

Um! The KT63 DOES have ramp test. It's on the little button top left with the x1/2, x1 and x5.
See picture...
[ElectriciansForums.net] Kewtech kt63 no trip function
 
If you're into the CU, perhaps dis the RCD outputs and test separately?
That’s a possible, rcds tested well though, highest 34ms at 1x lowest 14ms at 5x not overly quick or sensitive. No trips at 1/2. Whole installation is good and tests as you would hope to expect!
Um! The KT63 DOES have ramp test. It's on the little button top left with the x1/2, x1 and x5.
See picture...
[ElectriciansForums.net] Kewtech kt63 no trip function
doh yes of course it does! Deliberate mistake, honest.
 
I've never had a problem where my KT63 trips an RCD on no-trip loop (so far - not saying it'll never happen), though I have had issues where it refuses to take a test. This has usually turned out to be a problem with the neutral... for instance, this socket-outlet had a decent R1+R2 value, but would not do a no-trip Zs
[ElectriciansForums.net] Kewtech kt63 no trip function

You can see the degradation on the neutral terminal.

If you're having trouble measuring Zs on an RCD circuit, you can always use "The Alternative Method for Measuring Zs," using "high current loop" setting.
 
Interestingly, I've found that the KT63 will do a 2 lead "high current Zs" test on a circuit protected by a 100mA time delayed (type S) RCD without tripping it.
 

Reply to Kewtech kt63 no trip function in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
795
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
827

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top