Hi

Guys i'm doing a fault find/testing on a modular YMCA,these modular were pre-wired at a factory
& basically i've corrected all the wiring faults,i'm about to start dead testing but i'm a little confused.
The keycard supply is terminated Live & Neutral into the RCBO & obviously go to the key card,but the cpc has been brown sleeved & go to the A1+ on the contactor & the load on the keycard,the key card itself is double insulated,the circuit is wired in 2.5 3 core flex

As far as the test cert goes there is no earth so cant do a r1+r2 or Zs or do rcbo trip times?is this correct or is there some simple easy way around this?

Any help would be greatly appriciated.
 
Hi,
Just put N/A in the R1+R2 and Zs as you would do for any other class II item, and make a note ie. Class II in the comments as well as vunerable equipment.

You can still do the RCBO trip times at the RCBO in the DB/CU as you would normally do
 
Last edited:

Reply to Keycard Supply in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
894

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
950
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top