Just thinking about a kitchen circuit, How close would i be pushing a 32a rfc with washing machine, dishwasher, and two double sockets (likely to use kettle and toaster at the same time ) would 2x A3 circuits be more sensible?
 
Last edited by a moderator:
Pushing a 32A rfc? Seems like you are refering to a small kitchen. I doubt you'd have any problems at all with a 20A/2.5 radial.

Consensus seems to be that a whole kitchen is fine on a 32a circuit, (excluding cooker of course)

washer 10amp
dishwasher 10amp
kettle 13amp
toaster 10 amp
convection microwave - 10amp
tumble dryer - 10amp

total - 63amp, which potentially could easily all be used at the same time? (christmas day scenario). In reality, is it rare for such a setup to trip an mcb.
 
If I suggested that lot to my ex on a Christmas day my biggest problem would be “How the hell do I get out of this washing machine”!

Come on use common sense (and diversity).
 
Just thinking about a kitchen circuit, How close would i be pushing a 32a rfc with washing machine, dishwasher, and two double sockets (likely to use kettle and toaster at the same time ) would 2x A3 circuits be more sensible?

I run mine on a 6A breaker.

Quadruple that load then it might need thinking about.
 

Reply to kitchen 32a rfc or 2x a3 radial in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
853

Similar threads

  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
2K
Your kWh figures are giving you consumption averaged over each hour period, but don't give an indication of total instantaneous current. To try...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top