S
sparkydude
Called out today to a commercial kitchen hood. Fan runs through a speed control DOL starter with overload and is interlinked to the gas proving unit.
Fan tripped out today and took a while to reset. The kitchen manager said that he managed to get it to start again but it will not run on speed 5 as it then trips the overload unit. Would i be right in thinking the fan needs an overhaul as it seems to be drawing too much current due to being caked in grease?
Could not gain access to fan as its on the roof and in the middle of a garden centre !! The motor was drawing 6.8A on speed 4 and the overload uit it runs through had a maximum of 9A which it was currently set at .
I am pretty sure it comes down to the fan needing to be cleaned , but welcome anyones oppinion It sort of confused me that the overload was set at full load as i thought normally you would install one with some tolerance in the scale.
Nick
Fan tripped out today and took a while to reset. The kitchen manager said that he managed to get it to start again but it will not run on speed 5 as it then trips the overload unit. Would i be right in thinking the fan needs an overhaul as it seems to be drawing too much current due to being caked in grease?
Could not gain access to fan as its on the roof and in the middle of a garden centre !! The motor was drawing 6.8A on speed 4 and the overload uit it runs through had a maximum of 9A which it was currently set at .
I am pretty sure it comes down to the fan needing to be cleaned , but welcome anyones oppinion It sort of confused me that the overload was set at full load as i thought normally you would install one with some tolerance in the scale.
Nick