Hi All, first post here and looking for a bit of advice. I am planning on having a few changes done to the kitchen island.
wanting to add a quooker tap.
This is what I currently have in place;
Stating at the CU.
40a mcb > 10mm2 t+e > 60a junction box (at island) > 10mm2 t+e > 45amp mk switch > 7.8kw induction hob.
A few years ago when the extension and kitchen was done I asked for the cable to oversized to accommodate future changes incase we wanted extra hence the 10mm cable.
I have had local spark have a look and this is what he a suggested.
Swap over to a 50a mcb split the cable at the island a take a 10mm feed to a 20a switch and add the tap to this.
The spark has said it's a push getting 2 10mm cables into 60a junction box, he has suggesting using either Henley blocks inside an enclosure or using wago din terminals to split the 10mm cable.
I want to known what's the best option not the easiest or cheapest before I go back.
Any advice is much appreciated
Cheers
Matt
wanting to add a quooker tap.
This is what I currently have in place;
Stating at the CU.
40a mcb > 10mm2 t+e > 60a junction box (at island) > 10mm2 t+e > 45amp mk switch > 7.8kw induction hob.
A few years ago when the extension and kitchen was done I asked for the cable to oversized to accommodate future changes incase we wanted extra hence the 10mm cable.
I have had local spark have a look and this is what he a suggested.
Swap over to a 50a mcb split the cable at the island a take a 10mm feed to a 20a switch and add the tap to this.
The spark has said it's a push getting 2 10mm cables into 60a junction box, he has suggesting using either Henley blocks inside an enclosure or using wago din terminals to split the 10mm cable.
I want to known what's the best option not the easiest or cheapest before I go back.
Any advice is much appreciated
Cheers
Matt