rryles

Looking for some advise on how to supply some sockets on a kitchen island through a floor that will have wet underfloor heating.

The floor hasn't been started yet, so I've got the choice of which layer to install it in. The complete structure of the floor starting from the bottom will be: earth, sand, damp proof membrane, 100mm rigid polyisocyanurate insulation (kingspan/celotex style), Heating pipes in clips and covered in ~70mm cement screed.

I'm thinking of installing a duct in the insulation, deep enough to be out of the way of the pipe clips. I'm open to alternative suggestions though.

The rest of the sockets in the kitchen will be a 4mm² radial on a 32A MCB. As the cable will be quite heavily derated I'm considering a lower rated protective device for this (either a fused spur or dedicated radial). I could also do with a bit of help working out just how severely derated the cable needs to be. The closest I can see is reference method A, with an ambient temperature factor.
 
I would consider running a 25mm plastic conduit on top of the damp proof membrane but under the insulation, that way the conduit is as far away from the source of heat as practically possible and at it's worst will be fully surrounded by insulation for only 200mm of it's run. If it's run in 4mm i would guess you'll at least be able to bung 16A down it which would be more than adequate for a couple of sockets. I'm basing this partly on a derating factor of half for a cable fully surrounded with insulation for 500mm of its run. I don't think this figure is up to date as i think they reduced the derating factor for cables surrounded by thermal insulation in the 17th edition.
 
Unless you have a means of sealing your duct or cable through the DMP then you will have to install above it!! There's no need to go overboard on de-rating your cable(s) to this kitchen island. Use the standard de-rating factors you would normally use for finding a suitably sized cable etc. Use a heavy gauge duct, (with a decent space factor for the cable(s) as those thin walled pipes tend to deform with any sort of heat source....
 

Reply to Kitchen Island Supply with UFH in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
264
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
753
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
740

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top