P
Paultrim123321
Hi gents
Just wondering if anyone can advise me on my working out.
Have been asked to advise on supply conductor csa for a sub distribution supply. The power requirements are 10kVA 400V supply.
I'm used to working with kW power just not sure on kVA - Amps formula which I have used below: -
I = 1000 x kVA / (1.732 x VL-L(V)
Therefore 10000 / (1.732 x 210V)
Therefore 10000 / 363.72
Amps = 27.49?
I'm a little confused as if I transpose kVA - KW :-
kVA x PF
10 x 0.95 = 9,500kW
So if I use 9.5kW,
9500 / 1.732 x 400 x PF (0.95)
my design current drops to 14.43Amps?
Any advice would be great thanks all