Hi gents

Just wondering if anyone can advise me on my working out.
Have been asked to advise on supply conductor csa for a sub distribution supply. The power requirements are 10kVA 400V supply.

I'm used to working with kW power just not sure on kVA - Amps formula which I have used below: -

I = 1000 x kVA / (1.732 x VL-L(V)
Therefore 10000 / (1.732 x 210V)
Therefore 10000 / 363.72
Amps = 27.49?

I'm a little confused as if I transpose kVA - KW :-
kVA x PF
10 x 0.95 = 9,500kW
So if I use 9.5kW,
9500 / 1.732 x 400 x PF (0.95)
my design current drops to 14.43Amps?

Any advice would be great thanks all
 
Your 1st calc was almost right, but where did you get 210V from?
Your 2nd calc was almost right as well, notice that the power factors cancel out, so you don't need it!

Cheers Archy, I took 210V to be Line voltage - line voltage.
I see what you mean about PF! Doh:)
Have I miscalculated tho somewhere as if I work out kW from kVA my result is different, substantially when I transfer kW to amps? It as if I haven't root3 correctly?
 
kVA is exactly what it looks like: kilovoltamps, so when you divide VA by the voltage, by definition you get the current. Hence it being called the apparent power, i.e. what the power appears to be from multiplying the voltage and current, without any regard to the power factor.

Real power in kW is the apparent power in kVA multiplied by the power factor, so if your power factor is less than unity the load won't be able to do as much useful work but the circuit current must still be calculated from the apparent power in kVA, without involving the power factor.

Note that for 3-phase power calcs the quick way in your head, it's not necessary to put sqrt(3) in anywhere. Just divide the rating in VA by the line-neutral voltage to give the sum of the line currents, then divide by 3 to get the line current. In your case (10k/230)/3 = 14.5A. It's useful to remember that a balanced 3-phase load on 400V takes 1.45A line current per kVA.
 

Reply to kVA - Amps Formula for Three Phase in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top