I'm an apprentice electrican. Please could someone give me some guidance on this as I am confused? Thanks.

What is the difference between overload rating ie 6amp on a circuit breaker and breaking capacity on a circuit breaker ie 10ka?
I'm confused.

Thanks
:)
 
The 6 amp circuit breaker is designed to carry a continuous load of 6 amps without operating. If the device is subjected to a greater load than its rated current it will operate. How fast the device operates is dependent on how much it is being overloaded. Information regarding this can be found in BS7671 under the Time Current graphs. In regards to the 10KA this is the maximum amount of fault current the device can safely break. Although the device will not be good for continued use after this occurs.

I would advise if you do not already own BS7671 and the On Site Guide to purchase these.

Well worth joining the trainee section of the forum as well mate as there is lots of helpful people in this section:smile:
 
Under short circuit the mcb may be subject to a current of many thousands of amps... the Ka rating is what then device can cope with without failing - If you have a 6Ka mcb and a fault current under short circuit is higher than this the its possible the device could fail closed thus not breaking the fault.

As above the overload is the continuous current value that your circuit design should not exceed.
 
As above get the relevant documents and look for yourself it will be money well spent
 
In regards to the 10KA this is the maximum amount of fault current the device can safely break. Although the device will not be good for continued use after this occurs.

Breakers can potentially have two separate fault current ratings, Ics and Icn - I remember them as Ics(erviceable) and Icn(ackered). Ics is the fault current rating up to which the breaker can break and still be good for continued service. Icn will be a higher figure and is the fault current rating up to which the breaker can break but then be considered ruined. So for example you might get a breaker with an Ics of 6kA and Icn of 10kA.
 
Life gets difficult when you have breakers with separate Ics and Icn ratings cos if maximum prospective fault current is large enough to lie somewhere in the range between Ics and Icn (say Ics 6kA, Icn 10kA, max PFC 8kA) then for any given fault that tripped the breaker you can't be sure how big the fault current was and so have to chuck and replace the breaker as a precaution. Isn't life complicated?
 
Life gets difficult when you have breakers with separate Ics and Icn ratings cos if maximum prospective fault current is large enough to lie somewhere in the range between Ics and Icn (say Ics 6kA, Icn 10kA, max PFC 8kA) then for any given fault that tripped the breaker you can't be sure how big the fault current was and so have to chuck and replace the breaker as a precaution. Isn't life complicated?

Any decent designer would have specced the breakers to have an Ics higher than the PFC though.
 
the word was "repair" before private ryan was out of nappies. but either will do to describe a committee.
 

Reply to KVa and ka and overload. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
269
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
264
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
348

Similar threads

https://www.flipkart.com/pmw-circuit-breaker-4-0-amps-240-v-over-load-protector-push-reset-switch-1-unit-power-plug/p/itm9829ad58f0809...
Replies
1
Views
739
Ok, please be aware that I am a 'do-it-yourself-er,' so if this isn't the right place to be posting this thread, let me know where I should be...
Replies
0
Views
425

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top