Hi All I need to apply for a new 100a x 3ph&n supply but I need to know the kva equivalent and figured the quickest way to find out is to ask you guys. Thanks in advance.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Kw to kva conversion in the UK Electrical Forum area at ElectriciansForums.net
Hi All I need to apply for a new 100a x 3ph&n supply but I need to know the kva equivalent and figured the quickest way to find out is to ask you guys. Thanks in advance.
This ^you need to know the power factor of any equipment that is to be installed. . rule of thumb is 0.8. the divide the kW by the pf to get KVA.
230 v 100 A is definitely 23 kVA on a single-phase supply. A three phase supply with a line-to-neutral voltage of 230 v the kVA delivered is three times as much, 69 kVA. That would normally be described as 400 v 3-phase, which is 400v line-to-line, in other words the normal LV supply going down a street.
Cheers Tanker222. A simple answer to a simple question and now I know.
230 v 100 A is always 23 kVA, doesn't matter about the PF.