Am just wondering if someone can help me on this "The disc of an energy meter makes 600 revolutions per unit of energy. When a 1000W load is connected, the disc rotates at 10.2 revs per minute. If th load is on for 12 hours, hw many units are recorded as error?" I calculated the % error of the meter to be +1.796%. The answer proooided to the question above is "0.24kWh more".
Can anyone tell me how did they come out to the 0.24kWh?
10.2 X 60 X 12 = 7344
7344/600 = 12.24
Actual reading should be 12 so error is 0.24kWh
Giving a meter error percentage of +1.965% which is within current published acceptable tolerances of +2.5% and -3.5%.
7344/600 = 12.24
Many thanks for that IQ Electrical, very much appreciate it....
My % error calculation seem to be different from yours???
Reply to kWh meter manual testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Interesting what you say, I have allowed with my system for the change to be half hour out, so start charging at 0:30 and stop at 7:30 but night...
It sounds like the original meter was reading incorrectly and octopus aren't keen to admit this as they would probably have to refund you. I...