D
DurhamSparky
Right Chaps
Down Stairs lighting Circuit wired to a 6amp MCB
circuit goes like this
CU - Front Room - Kitchen (9 230v downlights) - Hall - Utility / Outside light - Office....
i know its a L-E fault as the little blighter zapped me on the Earth connection plus my meter reads 0.85 when 500V testing the thing!!
the job is a previous Bodge and so far have uncovered many of faults with the circuit! namely melted connector block and nicked cable's
I spent 4-5 hours on it so far and now its driving me insane!!
when the mcb is made it has a delay in tripping!! and some times stays on for 15 mins before going!! which makes it harder to fathom out!!!
im struggling!! bar telling the customer to rewire the circuit as its a mish mash of mess any sugestions!!
Down Stairs lighting Circuit wired to a 6amp MCB
circuit goes like this
CU - Front Room - Kitchen (9 230v downlights) - Hall - Utility / Outside light - Office....
i know its a L-E fault as the little blighter zapped me on the Earth connection plus my meter reads 0.85 when 500V testing the thing!!
the job is a previous Bodge and so far have uncovered many of faults with the circuit! namely melted connector block and nicked cable's
I spent 4-5 hours on it so far and now its driving me insane!!
when the mcb is made it has a delay in tripping!! and some times stays on for 15 mins before going!! which makes it harder to fathom out!!!
im struggling!! bar telling the customer to rewire the circuit as its a mish mash of mess any sugestions!!