Hi all,
I've recently had an occurrence on a shopfit job I've just finished in Spitalfields where as usual I was the only trade who was beaten with a whip to finish by the hand over date which obviously turned out to be pointless as there were chippies & painters etc there in the following few days, also some staff training took place.
In my rush I knowingly connected a 6mm radial to a 20A RCBO for a glass washer, with the intention to change it when I picked up the 32A from the wholesalers, which as it turned out I missed. The other thing I missed was "labelling the fuseboard"
During the staff training, the glass washer in the potwash kept operating the 20A RCBO due to overloading of the breaker & the board not being labelled caused a problem when the staff looked at the DB.
Genuinely interested to know your thoughts on physically labelling fuse ways, I know it's ideal but I usually rely on a schedule being with the DB & although I wouldn't have missed it in an ideal world, still finishing bits off & testing etc at 9 in the evening is to say the least 'not' ideal! So basically I'd like to know if anyone can point out what the regs say about it, as the client obviously made me feel a bit of a Tw&t about it.
Thanks guys, this is my first post so please be gentle with me!
I've recently had an occurrence on a shopfit job I've just finished in Spitalfields where as usual I was the only trade who was beaten with a whip to finish by the hand over date which obviously turned out to be pointless as there were chippies & painters etc there in the following few days, also some staff training took place.
In my rush I knowingly connected a 6mm radial to a 20A RCBO for a glass washer, with the intention to change it when I picked up the 32A from the wholesalers, which as it turned out I missed. The other thing I missed was "labelling the fuseboard"
During the staff training, the glass washer in the potwash kept operating the 20A RCBO due to overloading of the breaker & the board not being labelled caused a problem when the staff looked at the DB.
Genuinely interested to know your thoughts on physically labelling fuse ways, I know it's ideal but I usually rely on a schedule being with the DB & although I wouldn't have missed it in an ideal world, still finishing bits off & testing etc at 9 in the evening is to say the least 'not' ideal! So basically I'd like to know if anyone can point out what the regs say about it, as the client obviously made me feel a bit of a Tw&t about it.
Thanks guys, this is my first post so please be gentle with me!