this installation was carried out in the 1995 ish

advice please on what code should be issused for a server room and also floor sockets (althought server room and floor room are on sepearate circuits) wired in 2.5 / 1.5 TW&E as radials with no high integrity earth i.e only one earth conductor.

the floor socket circuits have about twelve pc pluged in !


and also there is wall sockets with ring circuits with PC's pluged in with no double earth terminals on the socket outlets.


any advice welcome
 
You first need to check the total earth leakage current on each of these circuits, they may need a separate suitably sized earth conductor to be run in. Not having the appropriate data in front of me, i'll leave to others, the parameters you need to be working too!!
 
thanks E54
anyone else with to help me out with more in fo on the observation code

I'm sure someone posted a guidance note on ''High Integrity'' earthing requirements not so long ago. Check the similar threads at the bottom of this page, One of those threads may have that link, or can help you via the posts....
 
Last edited by a moderator:
Gemini Fire Management are specialist suppliers of fire Gas suppression systems and water leak detection systems for high value risk areas. Gas suppression system clients include major banks and IT companies.


I'm a little confused here, ...What has ''Room Integrity'' got to do with high integraty earthing?? This is to do with room sealing for gas supression systems...

More spam crap is it???
 

Reply to lack of high intergrity earthing on computer socket radials in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
688
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
652

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top