Reading the installation instructions it states that a resistance test and an insulation resistance test have to be completed. No problem with the resistance test across the line and neutral through the foils that produces a figure well within the calculated tolerances for the area of film laid down. How is the insulation test carried out as there is no earth and the line and neutral are effectively the elements within the foils? I just know there is a simple solution..........
 
That's the simple solution I reached but the instructions state "test after the flooring is laid" which is tad disconcerting as the heating foils has disappeared under said floor!
 
Follow the manufacturers instructions if they are not available on site then download them or contact tech this way you can give a good judgement as to whether its been installed correctly .. their a hundreds of systems out there be it variants of the same brand or indeed different brands altogether so we can't give an informed answer without knowing which one you have.

Sorry you answered partly as i posted... contact the manufacturer then and ask them if the foil is the earth you can't connect it up without ensuring the foil has a good earth to it and as its now buried i think this is possibly going to be an expensive issue to correct. Ill reiterate though the instructions should explain if the foil is the earth.
 
Apologies, I did not complete my "that's the simple solution....". I was going on to say that it couldn't be the earth as the laminated foil (with line and neutral connections only) is laid on to a 6mm thick sheet of foam insulation and is therefore does not have a connection with earth. I take the point about contacting the suppliers tech team and will do so. But I'm left wondering if the insulation test requirement is a generic statement that is more appropriate to the wire based systems that the same organisation also sell.
 
Id be very surprised if the set up has no earth consider a fault to the floor that may be wet anyone turning the tap on in their bare feet (no sarky comments about why someone has a tap on their foot pls :) ).

It may be the case its double insulated but again check with the manufacturer is the best solution here if you don't have the info at hand.
 
It's a Swedish outfit called EBECO and despite reading their installation instructions over and over again the only reference to anything linked to an earth is the requirement for the "installation to be protected by a 30mA earth fault relay. The only occasion the word earth is used. What I'm now wondering is if in Nordic world a 6mm insulation sheet under and a 20micron film over is classed as double insulation!
 

Reply to Laminated Foil Underfloor Heating in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
814

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top