hi guys,

went to look a lamp blowing problem today

would a insulation resistance reading of 0.50 mega ohms on suspect lighting circuit with all lamps removed be the reason why 2 wall lights, 1 ceiling pendant and 1 bathroom lights lamps keep blowing. there are another 4 lights on the circuit which don't have any problems.

strange

cheers
 
First thing I would be checking would be the supply voltage to the house. I've come across light bulbs etc rated for 220V, in houses with a higher supply voltage, say 240V, the bulbs work, but only for a short time before they burn out.
I had this in my house, the transformer is in my garden, so I'm first on the line, I have a high voltage, 235V+, so I make sure any lamps I buy are rated for 240V, and not the more common 220V.
(PS, located in Ireland)
 
Check voltage as said above voltage surges would blow lamps as well no way of monitoring that had problems with this in past fitted loads of gu 10s in different areas same ones most places ok but others would blow in other areas head wrecking
 
Might be the fittings, ES can often be problematic, particularly the older they are. The little tabs in the fitting are spring loaded, over time they weaken & fail to make good contact with the lamp. Many GU10's are of very poor quality, why not have a go with CFL or LED lamps.
 
the two wall lights are ses golf balls. the bathroom light is a 40w capsule lamp and the other light is a standard bc. apparently they are all good lamps they keep putting in.

well i'm going back in the morning. going to fit two new wall lights and one new bathroom fitting. fingers crossed
 
Hi,

I know everybody talks about loose Neutrals, but that was exactly what happened to me some years ago. Lamps were constantly blowing in a foyer of an Office, traced it back to a loose Neutral in a JB; corrected that, not a problem since then,

Regards.
 

Reply to Lamps Blowing in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
369
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
929
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
😄 It wasn't the worst I seen over the weekend. Took the kids to Cumbria zoo whilst over there, and the toilets by the giraffes just had twin...
Replies
7
Views
982
Check the clearance between the back panel and/or terminal cover that you've removed. Look for small burn marks.
Replies
3
Views
495

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top