The building is supplied with a 6mm swa and only includes 4 double sockets and 8 lights. The steelwork has to be earthed but in what size? Never wired a building like this before ie with the steelwork. Anything else I need to know about regs wise?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Large Barn Earthing Metalwork in the Australia area at ElectriciansForums.net
6mm unless PME supply then 10mm
whats the barn used for, is it on a farm, is livestock to be housed in the barn?
A whole section (705) on Agricultural buildings in the BRB