last min 2391 | on ElectriciansForums
Guest viewing is limited
Discuss last min 2391 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
wrighty
leeds
alright,
im sitting the dreaded tonight and just going through some last minute bits and wanted to make sure im getting things right so ive a couple of questions.
first 1:
Ze = 0.4
the installation is carried out in multicore steel wire armoured cables, having 70degrees thermoplastic insulation cables with 2.5mm copper conductors. these cables are clipped direct to cable tray throughout the installation. one of the cores of the cable is used as the cpc.
CSA 1.5mm = conductor resistance 12.1
CSA 2.5mm = conductor resistance 7.41
Determine the expected value for Zs for one of the lighting circuits where the ambient temperature is 20dc and the circuit length is 35m.
my answer is:
7.41 x 2 x 35 / 1000 = 0.51
0.51 + 0.4
= 0.91Ohms
Zs= 0.91 ohms
is this correct or do i need to use the correction factor of 1.2 aswell?
cheers in advance guys
Looks like they are looking for the expected value from your meter taken at 20degrees.
Those resistance figures look like 20 degree figures also. So no correction, the 20% figures comes in when you look at the max ZS for an MCB and then have to reduce it by 20% and compare against your measured or calculated reading.
Good Luck, only tip i can add is read the questions very carefully so that you know what info they are giving you and where, if anywhere, it fits into the answer.
20% correction is used to go from the max allowed ZS in BS7671 to one that you can practically measure. Because the max ZS is at the installations max temp (one which you will probably never experience) Bs7671 lets you chop 20% off the max to measure it at a nominal temp of 20 degrees.
The Op says the circuit length is 35m. The circuit is made up of L and N so R1 would be 17.5m long and so Rn and so would R2.
I would think "circuit length" in question refers to distance from origin to point of use,therefore all conductors in that circuit are of that length. Imagine if similar question refered to a "ring final circuit",giving a total length,division of conductor length for each conductor to point of use would induce a migraine...
Reply to last min 2391 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Recommended Sponsor News
Hi everyone,