Hi all

Just come back from a job where ther was 12v in the earth wire on the stair 2 way (no where else in the house that i know of). The customer only noticed as they were getting a tingle through the metal switch. I cant figure this one out. So does anybody have any theories as to what is causing this? some solutions would be appreciated aswell.

Dont want to tear their house to bits without knowing what I'm looking for!
 
think a bit of further investigation required there mate as you shouldnt feel a tingle on 12v, what was your reference when measuring this? possibly a loose earth or neutral connection.
 
Hi all

Just come back from a job where ther was 12v in the earth wire on the stair 2 way (no where else in the house that i know of). The customer only noticed as they were getting a tingle through the metal switch. I cant figure this one out. So does anybody have any theories as to what is causing this? some solutions would be appreciated aswell.

Dont want to tear their house to bits without knowing what I'm looking for!



Colud do with some more help please!!!!!!!!!!!!!
 
Are you suggesting that there is 12V on the earth wire or a 12V differential (PD) between earth and line? If it's the latter then you looking at a "leakage" of around 228V down the earth wire.

Start by selectively isolating earch circuit at the DB, whilst measuring the PD, until you notice a change in potential, if you're lucky it'll isolate it to one circuit. (I'd guess it's some dodgy equipment on a ring/radial main, but could also be a defective RCD/RCBO).
 
Sorry if this repeats any thing above, I'm trying to get this done ASAP as internet conn is iffy here. I reckon this is due to unconnected CPCs and electro magnectic induction. If you have a cable carrying a current running next to a conductor doing nothing ( non earthed CPC) the doing nothing conductor will indiate a PD (voltage) relative to its proximity to the current carrying conductor, the length of its proximity etc. All that is needed is to earth the cpc and this troublesome, shocking but probably!! not dangerous voltage will disappear
 

Reply to Leakage to earth in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
162
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

I used to do a lot of this. My go - to was testing at the load side of isolators etc where possible. Although of course you'll find plenty of...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top