Discuss Leave 6mm Bonding on TT? in the Australia area at ElectriciansForums.net

C

cyberjunction

Hi All

Can someone please clarify for me? I have installed a circuit on a TT system but the gas and water only have 6mm bonding. Does this mean I have to upgrade it or just note it on the cert and advise the customer?

Many thanks
 
If your main earthing conductor is 10mm then 6mm is fine for the main protective bonding conductors and would not need to be noted.

If your main earthing conductor is >10mm then note it on the cert it will only need replaced if it shows evidence of thermal damage.
 
I thought the main earth (ie to the rod) only needed to be 2.5mm (4mm if no mech protection) for TT so 6mm main bonding is ok.

It is as Sintra said -The main protective bond on a TT must be a min of 6mm² and not less than half the size of the main earth. You are correct in saying that the min size of an above ground main earth is either 2.5mm² or 4mm² depending on mechanical protection, but if someone has unnecessarily installed a 16mm² that would take the MPB up to 10mm² - in which case you would do a risk assessment checking for overheating of the MPB and note on the cert if you wanted to stay it as 6mm² :)
 
thanks everyone main bonding is 16mm so technically is should be so 10mm then as I thought as half the size, the meter is outside - will have to upgrade i guess to be safe after i do a a risk assessment of course - thanks again all

ps not sure why they used 16mm as its only 2 meters from the meter!
 
could be cheaper to just reduce the size of the main earth lol maybe the last guy only had 16mm² on board or didn't know the regs for a TT :)


Edit - i really must type faster eh Tel? lol
 
Last edited by a moderator:
The actual size of the earth conductor doesn't matter.
It's the size that is required that matters.
So if after applying the adiabatic equation, it is determined that only 10mm² is required, but someone has installed 16mm². You still only need 6mm² for the bonding.
 
Last edited by a moderator:

Reply to Leave 6mm Bonding on TT? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
811
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
695
The power company only brings in 3 wires which is 2 live and 1 neutral wire. It’s our responsibility to add the ground rod to bond the neutral...
Replies
3
Views
605

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top