Hi, just finished a job installing 12no 100w led floods from ansell lighting and they are causing me problems. The lights are switched alternate over two switches, so one switch does 6 and so does the second. First of all I has them connected to a B10 crabtree loadstar mcb which tripped 9/10 times when switching on either switch line. Strange I thought, spoke to ansell lighting and they confirmed I needed a c type mcb. Great I thought, ordered a C10 and all my lights fired up no problem. Customer was happy and so was I. Had a phone call two days later, lights have tripped. Why is this? I can't find any power factor for these lights, so therefore can't work out the peak load upon start up. It's wired in 1.5 and has a zs of 1.82 end of line so can't go to a D type . Any suggestions? Can't go any further on the breaker size, and it's roughly a 70m run. Have thought of putting the circuit through a spur on a B16 breaker and leaving it with the 13a fuse to see if this gives it the leeway it needs....