Hi guys.

Came accross this issue and wondered if anybody else has experienced anything similar. Installed a new lighting circuit in some outbuildings and the customer supplied a little 10w LED flood light for one of them. Completed the installation and when the testing was complete energised the circuit. Turned the light switch on and the LED light came on (so far so good), but when I turned the switch off, the light started pulsing once every 3 seconds?

The light switch was IP rated with a location neon that would illuminate when the switch was off. The only thing that I could think off was that this was allowing enough current to flow to the LED driver (through the lit neon), but not enough to 'strike'. I've also had the same effect when a customer installed a replacement LED lamp, where the same switch was installed.

Installed a 30w LED flood light in another building, and it works fine (including turning off!). There were no other loads connected at the time just a bog-standard radial lighting circuit wired in SWA and surface clipped. It just seems to happen with low wattage LED lights/lamps.
 
Then it's probably the current through the neon charging the capacitors in the LED driver
 
I was thinking the same. But when I spoke to a work colleague all I got was a blank face! I'm glad somebody else has come to the same conclusion!

Drawing the same conclusion? Nah, more like stating the bleeding obvious!
Just chop the neon out or fit a dummy resistive load to dump the current somewhere.
 
I should think every electrician has encountered a variant of this problem these days, it's a common issue with LED and low energy lighting.
 
Didn't have this problem with a good old fashioned 500w halogen flood light! LED are still a new thing for us down here! ;)
 
Last edited:
it is the neon I had to remove the neon or run a neutral to the switch and connect the neon to that. come back halogen lol
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Cornwall

Thread Information

Title
LED light flashing?
Prefix
N/A
Forum
Talk Electrician Forum
Start date
Last reply date
Replies
11

Advert

Thread statistics

Created
BigSim,
Last reply from
Jimmyb,
Replies
11
Views
4,394

Advert

Back
Top