Alex G

-
Joined
Dec 6, 2017
Messages
2
Reaction score
0
Location
Derbyshire
So a long story short, someone I work with said they had a small 'Tingle' off a Lumineux LED panel. We took a couple down that we recently installed, and plugged them into a safe tester to check if there was any voltage flowing through them. Oddly enough, we read 90-95V AC to earth, straight off the metal back of the panel. This is strange, as the Driver's output is only 38v DC. This was the same for all the fittings we tested. I spoke to Lumineux, but the guy thought I was crazy! Even if they were all faulty (they are all working fine) where is the 90VAC coming from?

Any Ideas?
 
Check the case and PSU are properly earthed. Switch mode PSUs usually have a capacitor between live and earth which provides part of an EMF filter I believe. This causes some leakage to earth. If the PSU doesn't have a good connection to earth this will appear as a voltage on any exposed metal parts.
 
Thanks for the reply... The LED Driver is double insulated and does not have an earth... The driver is not giving out enough voltage to cause the back panel to have 90V even if the fitting wasn't earthed properly. These are all plug and play so there isn't an option to earth the fitting, unless I did it to the grid it's placed on. but still... where is the 90V coming from :tearsofjoy:
 
Try measuring between the output terminals of the driver and earth. I think class 2 PSUs have the input and output coupled by a capacitor, again as a suppressor of EMI.
 

Reply to LED Panel Strange problem.. in the The Welcome Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Hi all, This may is a little odd and may take some getting your head around but here goes... I measured around half the load current on two DC...
Replies
0
Views
436
Hi all. OK... Let me just try and clear a 1" square space on the screen inbetween all the highly intrusive ads.... On a site (NHS in fact) and...
Replies
0
Views
410

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top