@Pete999 have you not heard of Ductor testing?
High current low resistance testing.
Megger DLRO is a very common unit.
Mine is only 10A, but they are available up to 600A they stress the conductors to a higher level than the low current testing done by a typical MFT, or DMM.
They also offer a resolution much higher than those given by a typical MFT.
The way that EN 60204-1 is worded it is easily interpreted to require high current testing for all protective conductor networks.
A classic use for a Ductor was to test steel conduit when installed and utilised as the circuit cpc.