giddash

Hi All,
Can anyone please help me on how to identify incoming legs from out going legs on a ring wired in singles
your help will be very much appreciated.Thanks

Best Regards

Giddash
 
start from source ie db continuity test will confirm legs from db then its a case of testing from socket to socket may i ask why

I ask this question becos' of cross connection of the incoming live to the out going cpc and vise versal to find my R1+R2 value for the ring as i dont went to cross connect the live to the cpc of the same leg
 
Do your end to end measurements (r1, rn ,r2) then cross connect your lines and cpcs in connector blocks. Do a test between the 2 connector blocks. Your reading should equal (r1+r2) Ă· 4. If not you've probably got them the wrong way round.
 
Do your end to end measurements (r1, rn ,r2) then cross connect your lines and cpcs in connector blocks. Do a test between the 2 connector blocks. Your reading should equal (r1+r2) Ă· 4. If not you've probably got them the wrong way round.

The measurements will be the same.
 
split the ring , at approx. mid point. connect 1 leg to MCB. go back to where you split. ssee which leg bites. ( don't try this at home, children)
 
You'll soon know if you've got them wrong anyway as you should be getting the same reading at each socket. If not then they're the wrong way round. :wink:
 
Big Thank You to You all who have contributed to this thread. I appreciated your usefull toughts and suggestions.Thanks

Best Regards

giddash
 
easiest way is to ( with power isolated) spllt ring at any socket. short out l/e of each cable. then at DB, ohm meter l/e. that will give continuity of each leg's l to e. mark them up, reconnect the split, and away you go. repeat for l/n or n/e if you need to.
 
Hello m8!
Have you got an On site guide or an Guidance Note 3? Step 2 and 3 of continuity of ring final circuit will explain you how to identify incoming and outgoing legs.
 
Might just be me but the lives should be easy to ID does the OP not mean the N's & E's as they are all in the same bar and in singles, I know my heart sinks when I open up DB and see it,s all singles worse if it,s tri phase
Pict
 

Reply to legs identification in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
314
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
836
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
943

Similar threads

R
  • Article
Can anyone help me identify these bathroom taps please? Hi Can anyone identify the make and model of these taps please? We have one dripping...
Replies
0
Views
250
Richt5a
R
I'm not sure on the environmental implications, a good quality integrated fitting will last many years and be more energy efficient than the GU10...
    • Like
Replies
13
Views
1K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top