is this correct for lighting circuit of 1.5mm line and 1mm cpc
ze+R1+R2=zs

b6 mcb ze R1+R2
6.18ohms - 0.8ohms =5.38ohms


cable per meter = 0.03020ohms so 5.38ohms/0.03020=178.1M

does this mean my lighting circuit can be this length 178M and still be within zs value... cheeers if makes sense
 
Last edited:
i=p/u, not checked your calc. yet, but pleeeeease distinguish between r1,R1, etc. 2 different measurements!!!!!!!!!

also Ze and Zs mixed up mate. being picky i know, but you got to get it right terminology.
 
Last edited:
is this correct for lighting circuit of 1.5mm line and 1mm cpc
ze+R1+R2=zs

Correct

b6 mcb ze R1+R2
6.18ohms - 0.8ohms =5.38ohms

Dont apply a factor to the Max zs value, i presume you are using a tns .8

does this mean my lighting circuit can be this length 178M and still be within zs value... cheeers if makes sense

I think you will find volt drop your overriding factor
 
Circuit length would be limited by the circuit VD in this instance

As a rough guide assuming a load of 5A and a Ct factor of 1 gives a maximum length of 47.5M to comply with the 3% (6.9V) permitted VD.
 
As I said, rough guide.

I used a Ct value of 1 just as an example, which errs on the side of safety when in actual fact Ct will be less than one due to the CCC of 1.5mm T+E and the fact you would be limiting it to a max of 5A when it is capable of carrying more.

Also it is impossible to say what the ambient temperature of the area surrounding the cable will be........is it in an attic, under insulation etc etc, the OSG bases it's values on ideal situations but does make you aware in the notes associated to the particular table.
 
Last edited by a moderator:

Reply to length of cable runs in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
949
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
261
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top