Hi guys. When using a DC volt drop calculator, when it comes to the length of DC cable run,does that refer to the distance of the panels from the inverter or the distance of the cable from the - terminal of the inverter to the positive. As in the length of the single core circuit from positive to negative??

Thanks in advance
 
We take it as the TOTAL length of the DC cable in a string, so 2 x 900mm per panel, plus the run out (-ve) plus the run back (+ve) there again we've always been conservative on all our calcs ...
 
Thanks guys. It is a bit confusing. I was kind of thinking along the lines of Worcester but then thought than on an AC circuit you'd go with moggy1968's idea. Sedgy I agree, but I think the insulation will evaporate in a second on a 4mm from a 16 string combiner box ;) haha
 
yep, you don't include the length of the neutral on an AC circuit so why would you consider the length of the -ve on the DC?

imagine the sort of runs we've considered elsewhere, 300m+. that would end up being very expensive if you count the return path!
 
For DC, you're meant to consider the total cable length = positive + negative, because the 'same' current has to flow through both. With AC, the 'neutral' is essentially at earth potential, so only consider the voltage drop in the 'active' live line.
But it depends what voltage drop calculator you're using. For example in Sunny design, you only specify the single cable length for both AC and DC, but if you look in the project summary, you'll see that the program has doubled up the DC cable length you specified, when it calculates the voltage drop, whereas the AC is left as the single length value (even for three phase)
 
Our DC runs are often 150m - 200m plus round trip ... hence I've got a warehouse full of 6mm2 ( :) ) Our next job the runs are 45m out and back, total lengths therfore in the order of 150m or so per string, so yes I DO concern myself with the length and size of the cable.
 

Reply to Length of DC cable run in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
348
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
888
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

See there is the problem. I can put back to way it was. Is it safe, in my opinion NO!! It's wasn't safe before the incident. No Fused Spur...
Replies
9
Views
528
I can imagine it just disappearing (loudly) under short circuit conditions, then the resulting blast/plasma etc. casing the busbars to flash over...
Replies
13
Views
700

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top