Friend (honestly) of mine was given an observation on his yearly scam visit, something to do with the ring circuit being too long. Used r1 figure to work out length of cable I assume.

There's nothing in the BYB regarding this where else could this requirement be?
 
Friend (honestly) of mine was given an observation on his yearly scam visit, something to do with the ring circuit being too long. Used r1 figure to work out length of cable I assume.

There's nothing in the BYB regarding this where else could this requirement be?

Appendix 15 fig 15A Regulation 433.1.204 (iv) states taking account of the total floor area being served. (historically. a limit of 100 m2 has been adopted)
 
If he is unsure he must ask for clarification and justification.
Only reasons that spring to mind is that the length of cable does not satisfy Zs or volt drop requirements, or that the floor area served is too large.
This is worked out in the OSG table 7.1 to be 106m for a 32A B type, with certain conditions.
 

Reply to Length of ring in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
Replies
7
Views
1K
  • Question
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...
Replies
2
Views
494

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top