Hello there,
I'm currently taking my Level 3 and have been given an assignment to do which I have all most finished but I was wondering if anyone could use their infinite electrical knowledge and help me out with 3 faults that I need to identify and rectify? I will lay out below what I have so far written out and if anyone can point me in the right direction ill be well chuffed. Thanks
Ring 4 - On testing the ring where all the conductors are the same size they test (Note that this all the information available)
E1 and E2 = 2 Ohms
N1 and N2 = 2000 Ohms
L1 and L2 = 2 Ohms
The Fault
Now my first inclination is to say Open circuit on the Neutral because as we know from the question that all the conductors are the same size. An Open circuit situation would mean there is a break in the continuity of the circuit producing a an increased risk of an overload else were in the subset of the ring but could it also point out just a high resistance at one of the terminals? Or indeed more than one break in the neutral?
To Rectify the Fault.
Now I have idea how I would go about this but its is just trying to articulate it in away that doesnt take up the
Guys I had the answer written out for you lot to check but some reason the website only saved the top portion of my thread as it signed me out
Any ideas id appreciate it thanks
I'm currently taking my Level 3 and have been given an assignment to do which I have all most finished but I was wondering if anyone could use their infinite electrical knowledge and help me out with 3 faults that I need to identify and rectify? I will lay out below what I have so far written out and if anyone can point me in the right direction ill be well chuffed. Thanks
Ring 4 - On testing the ring where all the conductors are the same size they test (Note that this all the information available)
E1 and E2 = 2 Ohms
N1 and N2 = 2000 Ohms
L1 and L2 = 2 Ohms
The Fault
Now my first inclination is to say Open circuit on the Neutral because as we know from the question that all the conductors are the same size. An Open circuit situation would mean there is a break in the continuity of the circuit producing a an increased risk of an overload else were in the subset of the ring but could it also point out just a high resistance at one of the terminals? Or indeed more than one break in the neutral?
To Rectify the Fault.
Now I have idea how I would go about this but its is just trying to articulate it in away that doesnt take up the
Guys I had the answer written out for you lot to check but some reason the website only saved the top portion of my thread as it signed me out
Any ideas id appreciate it thanks