EddieB

-
Arms
Joined
Nov 3, 2008
Messages
290
Reaction score
23
All
Just replaced a Consumer unit new tails etc etc, when the electric shower kicks in it causes the lights to flicker.The shower is 9kw and is run in 6mm distance of about 8m. I have checked for loose connections. I'm going to load test with a clamp meter but I'm not expecting anything out of the ordinary. Any ideas anyone?
 
you will get a flicker on the lights when that sort of load is suddenly switched on ,having said that this could be a problem with a neutral at the icomming supply do a Ze test and see what the readings are any higher than youd expect call out the DNO as prevention is better than cure !! oh just a though check the bus bar connections on the mcb's its possible the bus bar has missed the clamp on the MCB
 
Last edited by a moderator:
Don't see how cable size would affect the stated problem which is flickering lights.
What is the duration of the lights flickering? Are they flickering all the time the shower is on, or just when it is switched on?
 
Don't see how cable size would affect the stated problem which is flickering lights.
What is the duration of the lights flickering? Are they flickering all the time the shower is on, or just when it is switched on?

Yes, this is the key question, a flicker on start/stop is normal 'inrush', a constant flickering would probably indicate a loose connection arcing under the increased load.

I had this on a call-out only a few weeks ago and it turned out to be on the line terminal on the meter!
 
Hi all
Cable size isn't an issue, connections all seem ok, I'll have a look at the incoming supply termination tightness etc, the Flicker is only for the initial switch on, but i have the same set up at my place and no flicker there.
 

Reply to Light Flicker in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
790
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
813

Similar threads

The lights are on a circuit with other lights, which is a different circuit from this receptacle. Both of these circuits and others are on the...
Replies
2
Views
1K
Adding a led strip isn't going to make much difference to the 3 phase balance. No real difference to where a 3 phase machine uses one phase to...
Replies
2
Views
317

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top