I am working in a property that has the old steel painted switch back boxes that have no earth terminal. Came to light when testing R2 on the switch faceplate screws and got open circuit reading. Earth is present but just sleeved and folded over in the back box.

I intend to ring crimp the earth and clamp it under the fixing screws holding the back box into the brickwork, removing paint under the ring crimp to give good conductivity. Tested one and got a good R2 reading on the screws. Is this an acceptable method, obviously I don't want to start ripping boxes out the wall to install new galv back boxes.
 
or you could replace switches with metal facepates and use the earth terminal in the new faceplate. the 3.5mm pins would then give you an earth to the box.
 
I wouldn't put them under back box screws it isn't an earth terminal. Some back boxes have four lugs for front plate fixing and you could use one of them or drill and tap the back boxes but the brickwork gets through the drill bits. The previous Post to this is an excellent solution.
 
Yes, there are only 2. So would you comment on this under condition of existing system on the EIC and state what solution I have provided?
I would C3 that the cpcs are terminated under back box fixing screws. I would drill and tap them.
 
I can't to find a reg which would not permit what I am proposing. 134.1.4 seems ok and 526 i dont see anything there.
what about the fixing screw rusting over time and creating a high resistance contact. even if i say so myself. my post suggesting metal faceplates is a good solution and also improves the aesthetics. win win.
 
Most of the black painted switch boxes around here have plastic lugs so is not a problem, I take it yours have metal lugs though?

There is a reg which says a fixing screw can't double as an earth terminal, though I've no Idea which one. If the box gets knocked it could loosen the connection etc. Unlikely with a recessed box though. In the stores we have a load of MK earth terminals that would do the job, though the box would have to be removed from the wall to do it by which point it would be easier to replace the box!
 

Reply to Light Switch Back Boxes with no earth terminal in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
317
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
842
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
965

Similar threads

Thanks Brian. I'll keep doing it then, no harm I suppose. I am lucky in that being DIY, I have the luxury of time when it comes to this kind of...
Replies
4
Views
2K
  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
768

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top