I am working in a property that has the old steel painted switch back boxes that have no earth terminal. Came to light when testing R2 on the switch faceplate screws and got open circuit reading. Earth is present but just sleeved and folded over in the back box.
I intend to ring crimp the earth and clamp it under the fixing screws holding the back box into the brickwork, removing paint under the ring crimp to give good conductivity. Tested one and got a good R2 reading on the screws. Is this an acceptable method, obviously I don't want to start ripping boxes out the wall to install new galv back boxes.
I intend to ring crimp the earth and clamp it under the fixing screws holding the back box into the brickwork, removing paint under the ring crimp to give good conductivity. Tested one and got a good R2 reading on the screws. Is this an acceptable method, obviously I don't want to start ripping boxes out the wall to install new galv back boxes.